SL 2000 duct smoke detector
« on: January 21, 2015, 08:55:07 PM »
Has anyone install the above duct smoke detector?I was looking at the diagram but looks a bit confusing.Any tips.

Offline Admin

  • Administrator
  • *****
  • Posts: 1894
    • HVAC TECH GROUP
Re: SL 2000 duct smoke detector
« Reply #1 on: January 22, 2015, 07:17:56 PM »
I haven't used one myself.  What are you trying to do with it?  Is it being connected to a fire alarm control panel?  What type of system are you working with?  air handler, gas furnace, rooftop?

I found the SL-2000 instruction manual, and it's not the greatest.

Are you trying to stop the fan if the detector goes off?

It looks like you would wire a 24V source to terminals 9 and 10 on the detector.  You could use R and C as a source or install a new transformer.  Then you tie into G to interrupt the fan by wiring it in series to terminals 7 and 18 on the detector.  If the detector went off terminals 7 and 18 would open and stop the fan.

You could also interrupt a 120V or 230V fan motor.  Make sure the neutral wire goes to the 115 terminal and the hot wire goes to the H terminal if you're trying to stop a 120V fan motor.

Then you would just tie into the fan motor's neutral wire and connect it in series to terminals 7 and 18 on the detector.  The fan motor would stop running if the detector went off.

Is this a residential or commercial job?

Offline harshal

  • 313D Supporter
  • ****
  • Posts: 104
Re: SL 2000 duct smoke detector
« Reply #2 on: January 23, 2015, 01:44:56 PM »
Its residential job.i am trying to cut off the furnace in case the smoke comes off in the duct for whatever reason.I think that explanation will help me a lot.
Thx.

Offline Admin

  • Administrator
  • *****
  • Posts: 1894
    • HVAC TECH GROUP
Re: SL 2000 duct smoke detector
« Reply #3 on: January 23, 2015, 01:54:21 PM »
Good stuff!

You could also tie into R to kill the entire system or W to cut the heat.


Offline harshal

  • 313D Supporter
  • ****
  • Posts: 104
Re: SL 2000 duct smoke detector
« Reply #4 on: June 07, 2017, 10:42:42 AM »
Is someone use the duct smoke detector other than SL 2000?Some city has the bylaw requirement to install on the furnace for legal basement requirement.