Author Topic: Gas line  (Read 396 times)

Offline harshal

  • 313D Supporter
  • ****
  • Posts: 113
Gas line
« on: May 01, 2017, 02:12:46 PM »
Is there any requirement for the gas piping for the above ground? What is the min requirement fron the ground? When the gas piping is located outdoor and before entering the home.precisely the piping is between the meter and before entering the home.

Offline Admin

  • Administrator
  • *****
  • Posts: 2052
    • HVAC TECH GROUP
Re: Gas line
« Reply #1 on: May 01, 2017, 02:27:10 PM »
There is no minimum height requirement from the exterior gas pipe to grade, it just can't touch the ground.

Enbridge no longer wants piping run low along the wall in garages due to vehicular damage though.

Download the Builder's Technical Bulletin here - http://www.hvactechgroup.com/article.php/20140405102136638