How does everyone test limits and safeties and pressure switches. I usually test the limits and rollout with a lighter and to test the pressure switches I take the tube off. Was told that we should be recording temps at which switches trip and pressures when pressure switches make or break. Any thoughts on this? Not trying to be paranoid but don't want to get any issues with tssa

Offline Mmtc79

  • Pro Techâ„¢
  • *****
  • Posts: 31
Re: Safety testing on equipment
« Reply #1 on: October 11, 2017, 07:05:45 PM »
Pressure switches can be tested with manometer limits by disabling fan

Offline mattmctree

  • 313D Supporter
  • ****
  • Posts: 82
Re: Safety testing on equipment
« Reply #2 on: October 12, 2017, 06:58:31 AM »
Do you keep records of the temps and pressures that they trip at on your service report or is that nescesary

Offline Mmtc79

  • Pro Techâ„¢
  • *****
  • Posts: 31
Re: Safety testing on equipment
« Reply #3 on: October 12, 2017, 11:18:20 PM »
Yep also gas pressure and manifold pressure also temp rise ect plus photos also