Looking for the manual for this York unit.model TCGF42
S41S1A.
Also another question coming up that would you guys always replace the filter drier on 410 a unit when u would do a major repair like fixing a leak in a coil or service valve.it can be time consuming if the filter drier located in the condenser especially.any exception not to re the filter drier?
You can download the York TCGF manual - Here (http://www.hvactechgroup.com/hvacforum/index.php?topic=749.msg1980#msg1980)
QuoteThe practice of replacing the filter-drier every time the system is opened is particularly important on R-410A systems because of the hygroscopic nature of the oil used.
Thats true but rather than removing old filer drier if u install one more filter drier outside the condenser where is easily accessible ?
It is imperative that you replace the filter drier on a 410A system when ANY system repairs are done. The POE oil loves to retain moisture and the only way it can be removed is to replace the drier. I made it a habit to put one size larger in to ensure all moisture was removed.
I would remove the factory drier and replace it and not leave it in, because it might be partially plugged or the dessicant might be full of moisture and could act as a restriction to the system.
Trainerguy