HVAC Forums => HVAC Help => Topic started by: nash668 on August 29, 2016, 07:53:16 PM

Title: Ductless Split Condensation Leaking Onto Wall...
Post by: nash668 on August 29, 2016, 07:53:16 PM
Friend of mine says his ductless split condensation is not catching in drain pan and leaks onto wall. I haven't had the chance to look at it yet but would love some opinions or suggestions on what to check or/and what to do.

Thanks!
Title: Re: Ductless Split Condensation Leaking Onto Wall...
Post by: Admin on August 30, 2016, 04:41:10 AM
It could be as simple as a blocked drain line or there could be a refrigerant leak causing the indoor coil to ice up and leak water.
Title: Re: Ductless Split Condensation Leaking Onto Wall...
Post by: walker on August 30, 2016, 06:41:44 PM
I ran in to one of these last week, 4th tech there in the last 2 weeks, the previous 3 techs all thought clogged condensate and blew it out with nitrogen.

Turned out to be  the drain line ran out the wall about 15ft, complete with a couple dips in the line, essentially creating a double trap, I added an air vent to the drain about a ft below where it exits the wall and re routed the drain line to not have dips.

no more condensate back up and customer is happy.