HVAC Forums => Technical Information => Topic started by: harshal on February 12, 2017, 04:58:22 PM

Title: Lennox modulating furnace
Post by: harshal on February 12, 2017, 04:58:22 PM
Working on the Lennox modulating furnace with the communicating thermostat and it been locking up with calibration issue for the low pressure switch.the model number of the unit is SL98UH090v36v-01.checked the vent and air intake both are clear.any thoughts?



Title: Re: Lennox modulating furnace
Post by: Admin on February 12, 2017, 06:50:54 PM
How does the drainage system look?

Lennox has had their share of pressure switch problems.  I would try replacing that.

The manual says for upflow installations the P-Trap can be installed on either side of the furnace, but I have read where installing it on the left side can cause problems.
Title: Re: Lennox modulating furnace
Post by: walker on February 12, 2017, 08:10:21 PM
check the pressure ports themselves, had more than a fair share of those plug up with crap, I usually take my tiny screwdriver and poke it through the port a few times to clear up any crap in there.  I have also had an instance where the board itself was just giving that false error and changing the board fixed it
Title: Re: Lennox modulating furnace
Post by: Sergroum on February 17, 2017, 04:48:17 AM
Dont forget that on this furnace there are actually two holes behind the Ventor Motor on the collector box. There is the big huge hole that you cant miss and a tiny one that can be missed easily and can get plugged up with crap.


SLP98 is pretty known for having very crappy pressure switches. They've released a (hopefully) improved version. I think they just changed the location of the port for one of the tubings there.