HVAC Forums => HVAC Help => Topic started by: mir on March 12, 2017, 10:53:48 PM

Title: Blower keeps running but burners shut off during call for heat
Post by: mir on March 12, 2017, 10:53:48 PM
Blower fan keeps running but burners shut off during heat call between 3-4 mints of initial start up.
Replaced the filter which was fully blocked but problem is consistent. Any suggestion
Title: Re: Blower keeps running but burners shut off during call for heat
Post by: Admin on March 13, 2017, 04:09:39 AM
Do you see a LED light, on the furnace control board,  flashing a code?  Have you tried cleaning the flame sensor?
Title: Re: Blower keeps running but burners shut off during call for heat
Post by: mir on March 13, 2017, 11:17:09 AM
Yes i have cleaned flame sensor. Burner come on for 4 mint when first start and than blower fan keeps running, thermostat in on auto. Can this be faulty limit switch?
Furnace model: c9mpd075f12c2
LED Code: 3 blinks
Title: Re: Blower keeps running but burners shut off during call for heat
Post by: Admin on March 13, 2017, 01:14:10 PM
It's a low pressure switch lockout code, according to the ICP C9MPD manual (https://www.questargas.com/ForEmployees/qgcOperationsTraining/Furnaces/Day&Night_N9MP%20C9MP%20H9MP%20T9MP.pdf).

Check that your venting is clear and sloped properly, and check the P-trap and drain line are clear.

If those things checkout use a multi meter and manometer to verify if you might have a faulty control board or pressure switch.