Hello
The unit being installed, Navien NHB-55 has a LWCO installed internally.
Is there one required outside as well.
Thanks
James
I believe BC uses the same B149.1-15 Code as Ontario.
The Navien NHB-55 is equipped with a pressure-sensing LWCO, so I believe you would require an external LWCO, as per Clause 7.1.13, if components were located below the boiler.
See this thread,
http://www.hvactechgroup.com/hvacforum/index.php?topic=2377.0
Thanks for the input.
Can't go wrong by installing one.
James