I have a customer with an apartment over his garage and he wants a furnace and ductwork. The mechanical room will be in the garage. Can I do that?
Yes, as long as the appliance is protected from damage.
Quote4.16.1 - An appliance in a garage shall be protected against damage.
Quote4.16.2 - In a storage garage, except for an appliance certified as flammable vapours ignition resistant (FVIR), an appliance shall be installed so that a component capable of igniting a flammable vapour is located not less than 18 in (450 mm) above the floor.
And you may have to hang it horizontally to satisfy Clause 4.16.2. If you can build a separate encloser then the furnace can be installed on the ground in the upflow position.
What about the ductwork? I was thinking about a room with a weatherproof door and the entire ductwork separated from the garage by finished drywall.
You will be fine if you do that. Here are the return air Codes found in the Gas Code and Building Code.
QuoteGAS CODE
(4.16.4) Where a forced air appliance for heating of the attached residential building is installed in a residential garage, no opening shall be located in the portion of the appliance return air system located within the garage and the return air system shall be made air tight to prevent the infiltration of air from inside the garage.
(4.17.2) Return air ducts installed in an enclosure shall be in accordance with the provisions set out for duct systems in the National Building Code of Canada.
(7.13.3) Return-air inlets shall not be installed in an enclosure or crawl space that provides combustion air to a furnace.
(7.26.7) Except for direct-vent water heaters, when the water heater is used in a combo heating system, return-air inlets shall not be installed in the same enclosure that contains both an air handling unit and the water heater. Adequate combustion air shall be provided for the water heater.
(7.26.8) When the return air duct(s) of an air handling unit in a combo heating system is installed in an enclosure in which any spillage-susceptible appliances are located, it shall be sealed to the air handling unit casing, and joints in the ducting shall be sealed to prevent infiltration of air from the enclosure into the return-air ducting.
BUILDING CODE
6.2.3.20. Return-Air System
(1) The return-air system shall be designed to handle the entire air supply.
(2) Where any part of a return duct will be exposed to radiation from the furnace heat exchanger or other radiating part within the furnace, such part of a return duct directly above or within 600 mm of the outside furnace casing shall be noncombustible.
(3) Return ducts serving solid fuel-fired furnaces shall be constructed of noncombustible material.
(4) Where combustible return ducts are permitted, they shall be lined with noncombustible material below floor registers, at the bottom of vertical ducts and under furnaces having a bottom return.
(5) The return-air system shall be designed so that the negative pressure from the circulating fan cannot affect the furnace combustion air supply nor draw combustion products from joints or openings in the furnace or flue pipe.
(6) Return-air inlets shall not be installed in an enclosed room or crawl space that provides combustion air to a fuel-fired appliance.
6.2.4.7. Return-Air System
(1) The return-air system shall be designed to handle the entire air supply.
(2) Except as provided in Sentences (3) and (4), return ducts shall be constructed of material having a surface flame-spread rating of not more than 150.
(3) Where any part of a return duct will be exposed to radiation from the furnace heat exchanger or other radiating part within the furnace, such part of a return duct directly above or within 600 mm of the outside furnace casing shall be noncombustible.
(4) Return ducts serving solid fuel-fired furnaces shall be constructed of noncombustible material.
(5) Combustible return ducts shall be lined with noncombustible material below floor registers, at the bottom of vertical ducts and under furnaces having a bottom return.
(6) Spaces between studs and joists used as return ducts shall be separated from the unused portions of such spaces by tight-fitting metal stops or wood blocking.
(7) A vertical return duct shall have openings to return air on not more than 1 floor.
(8) A public corridor shall comply with Sentences 6.2.3.9.(4) and (5).
(9) The return-air system shall be designed so that the negative pressure from the circulating fan cannot affect the furnace combustion air supply nor draw combustion products from joints or openings in the furnace or flue pipe.
(10) Return-air from a dwelling unit shall not be recirculated to any other dwelling unit.
(11) Except for floor levels that are less than 900 mm above or below an adjacent floor level that is provided with a return-air inlet, at least one return-air inlet shall be provided in each floor level in a dwelling unit.
(12) Provision shall be made for the return of air from all rooms by leaving gaps beneath doors, using louvred doors or installing return duct inlets.
(13) Return-air inlets shall not be installed in an enclosed room or crawl space that provides combustion air to a furnace.
Here are the taping Codes from the Building Code.
Quote6.2.4.3. Construction and Installation of Ducts and Plenums
(11) Where a supply duct or return duct is located in an unconditioned space or outdoors, all joints of the ductwork shall be sealed to a Class A seal level in accordance with the SMACNA, "HVAC Duct Construction Standards – Metal and Flexible".
(12) Where a supply duct is located in a conditioned space, the ductwork shall be sealed to a Class C seal level in accordance with the SMACNA, "HVAC Duct Construction Standards – Metal and Flexible".
Wow, thanks admin. Very much appreciated.