What section of code is this?
A or b tag ?
No CO leaking into room
I could understand if someone issued an A tag but personally I would issue a B tag. Maybe reduce the days to 15, on the B tag, to be certain it's fixed before it became an immediate hazard.
I believe you have done your diligence and proved it's not an immediate hazard.
Whats the proper section of the code
For a B tag use,
QuoteClause 4.1.3 - An appliance, accessory, component, equipment, or any other item shall be installed in accordance with the manufacturer's certified instructions and this Code.
The venting installation manual would require that the joint be properly glued.
For an A tag use,
QuoteClause 4.5.2 - The use of an appliance, accessory, component, equipment, or material shall be prohibited where a hazard is created.
Up to tech to decide how many days ??
Also whats o.reg # ?
You decide how long for a B Tag. Enbridge allows up to 42 days.
https://hvactechgroup.com/article.php/20150501132753661
Ontario Regulation 212/01 and 215/01 are 2 regulations you should read.
https://www.hvactechgroup.com/hvacforum/index.php?topic=325.0
https://www.hvactechgroup.com/hvacforum/index.php?topic=1212.0
The tag that ubpisted in that link doesn't even ask for a o.reg # ? Maybe mine are old....
Quote from: Admin on December 07, 2020, 12:10:02 PM
You decide how long for a B Tag. Enbridge allows up to 42 days.
https://hvactechgroup.com/article.php/20150501132753661
Ontario Regulation 212/01 and 215/01 are 2 regulations you should read.
https://www.hvactechgroup.com/hvacforum/index.php?topic=325.0
https://www.hvactechgroup.com/hvacforum/index.php?topic=1212.0
Did you read O.Reg 212/01? No where does it say the warning tag must specify O.Reg 212/01.
The rules for issuing a warning tag are very clear. Just read that regulation.
I ll post a pic of the tags i have later . Thx
Quote from: Admin on December 10, 2020, 04:04:39 PM
Did you read O.Reg 212/01? No where does it say the warning tag must specify O.Reg 212/01.
The rules for issuing a warning tag are very clear. Just read that regulation.
That's probably a TSSA tag. Both tags are fine to use.
All you have to do is what is listed in O.Reg 212/01 Section 13(3) and Section 14(3).
Yup that is what I was trying to get an. Hpw this one asks fornthrno reg #
Thx