HVAC Forums => HVAC Help => Topic started by: YYZ342 on May 27, 2021, 08:28:54 AM

Title: vanEE 1001 Gold Series + ComfortSync A3 (S30) Tstat
Post by: YYZ342 on May 27, 2021, 08:28:54 AM
Hey Folks,

I am trying to wire vanEE1001 with Lennox's ComfortSync A3 tstat. The erv has wall controls, the push button type, that start the erv for 20mins. They are connected to I, OC and OL.

I found this post from 2019 about similar situation. I connected ACC1 to G and B as suggested. The erv and the furnace blower turn on together when tstat is set to Ventilate Always. If I set the tstat to Timed mode or ASHRAE mode ventilation starts just the furnace blower. If I push the wall control it turns just the erv but that is expected as erv is not interlocked with the furmace.

The wiring diagram from Lennox shows a jumper between R and ON. Which one is ON on the ERV board?

https://www.hvactechgroup.com/hvacforum/index.php?topic=2702.0;prev_next=prev#new

What is the right way to wire them two, please help. I am not an HVAC guy but do OK around a house.

Thnx!
Cheers.