Post by: rcflightcrazed on March 21, 2022, 10:55:10 AM
Ok, I've been working on ACS for close to 30 years.  This one has me scratching my head.  New condensing unit was installed last year, has been running great.  Stopped working, I found the transformer was burned out, replaced it.  Now, I have my 24v outside, but as soon as I hook it to the contactor, it drops the voltage to about 1v. Installed new contactor, same thing, even with no high voltage wires hooked up.  T stat was replaced too, just because it was old, and I wanted to eliminate it as an issue.  Any suggestions?
Title: Re: Rheem condenser low voltage issue
Post by: rcflightcrazed on March 21, 2022, 01:16:44 PM
Got it!  Brand new contactor bad, out of the box.  Had me pulling my hair out! Up and running, 👍🏼
Title: Re: Rheem condenser low voltage issue
Post by: Admin on March 21, 2022, 02:59:53 PM
Good job.  That would have been my guess but you beat me!  ;D
Title: Re: Rheem condenser low voltage issue
Post by: hvactech83 on March 22, 2022, 05:53:41 PM
yes this happend to me one also with brand new contactor .
Title: Re: Rheem condenser low voltage issue
Post by: Hvacpimp on March 24, 2022, 08:04:49 PM
Good to know with the upcoming ac season. Thanks for the heads up!