I need to replace my Trane XL802 thermostat with the new Honeywell RTH9585WF I purchased. I can't find a wiring diagram that is the same as mine therefore I can't map the wires to the right place on the new thermostat. I've attached a photo of my current device (and wiring) and pic of the new wiring panel. Can anyone just map the 9 wires from my current set up to the right places on the new thermostat? Thanks in advance for anyone's help!
S1 and S2 are likely wired to a proprietary outdoor sensor you can no longer use with the new thermostat. The new thermostat WIFI should gather the outdoor temperature, so you can eliminate those 2 wires. You likely need to use one of them as your C wire now. Disconnect it from the sensor and connect it to the C terminal in the furnace and then the other end to the C terminal on the thermostat.
X2 is the AUX wire (AUX/E) and B is the reversing valve (O/B). There will be a thermostat setting to change the reversing valve to energize on heating or cooling. You may also have to adjust the thermostat and cut off temperature if you're running a dual fuel heat pump system. The other wires should just connect the same. R, W1, W2, G, Y.