Title: High Efficiency Furnace Venting Through Cold Air Return
Post by: rkeaner on January 28, 2023, 09:21:35 PM
My exhaust and intake vent pipes are in a terrible position for finishing my basement soffit. They run under my heat and return trunks and then up between floor joists to the outside wall. It looks like I can maintain the the correct slope if I go up and over the heat and cold air return trunks, however, I would have to go between the floor joists through one of the branches off the cold air return for a couple feet. Can I do this?
Title: Re: High Efficiency Furnace Venting Through Cold Air Return
Post by: Admin on January 29, 2023, 04:27:46 AM
The B149.1-20 Gas Code would not allow this in the province of Ontario,

QuoteClause 8.10.12 - A flue gas vent or a vent connector shall not be installed in either a duct or a shaft used for return air, hot air, ventilating air, or combustion air.

If the joist is lined and acting like a return air, you could just buy some duct board and reduce its size and box out the venting, so the venting was outside of the return air cavity.
Title: Re: High Efficiency Furnace Venting Through Cold Air Return
Post by: rkeaner on January 29, 2023, 10:08:04 AM
Thank You for response.  I assumed that was the case but hoped it was not.