HVAC Forums => HVAC Help => Topic started by: bdiddy1 on June 13, 2007, 08:49:57 AM

Title: pressure problem
Post by: bdiddy1 on June 13, 2007, 08:49:57 AM
wuzup new to doin service i have a brand new westinghouse 5 ton duelpack good air flow compressor kicks on but not cold enough pressure is 35/215 the low side is starten to freeze im thinking something is cloged, but it brand new any suggestionss thanks
Title: Re: pressure problem
Post by: TECH X on June 13, 2007, 08:40:19 PM
Anything below 60psig on your low side will have a saturation temp. lower then 32F, that's why your icing up.

Check that the underside of the evaporator is clean.
Could be undercharged, could have a metering device blockage or liquid line restriction. 

Would need to know your ambient temp, and indoor wet bulb, superheat and subcooling.

Here's a trobleshooting chart that might help,

(http://hvactechgroup.com/files/ACchart.jpg)

Title: Re: pressure problem
Post by: ProTemp on June 19, 2007, 04:55:23 PM
Use the force (temp probe and gages) young padewan..... :D