Title: Inducer cycling non stop
Post by: Tylergm on September 22, 2024, 10:05:29 PM
Hi, first time user here. The inducer motor on my old furnace cycles on and off both when there is no call for heat, and also when the furnace is providing heat to my house. An HVAC guy told me that my thermostat was faulty. I replaced it and it continues to have a problem. I have a basic understanding of the sequence of events that a furnace goes through and I can not understand what would be causing this problem. Especially because the furnace continues to provide heat when the inducer motor goes on and off repeatedly.
Title: Re: Inducer cycling non stop
Post by: Admin on September 23, 2024, 05:17:11 AM
I have seen this problem a couple times with some Honeywell thermostats and control boards.

Installing a bleed down resistor between W and C at the furnace may solve the problem.
Title: Re: Inducer cycling non stop
Post by: Porcupinepuffer on September 29, 2024, 01:44:02 PM
Disconnect the low voltage wire from the W terminal and observe the furnace. If the problem still continues, it's the control board.