Title: furnace sizing
Post by: Hp on April 09, 2025, 10:31:45 AM
how to size a high efficiency 2 stage furnace replacing a single stage 90,000 BTUs natural draft furnace. How many btus needed for new high efficiency furnace

thanks
Title: Re: furnace sizing
Post by: Admin on April 09, 2025, 01:59:43 PM
Where is the house located and how old is it?  And what is the input/output of the existing furnace?

Without a heat loss calculation it won't be scientific but I can probably get you in the right ballpark.
Title: Re: furnace sizing
Post by: Hp on April 15, 2025, 11:37:57 AM
its in Malton and build before 2000. 90,000 input to 82,ooo btu out
Title: Re: furnace sizing
Post by: TexMex099 on May 09, 2025, 08:33:03 PM
other calculations are typically done like duct sizing, sq footage and heat loss but if youre replacing it with lets say a 96 AFUE furnace then an 80k would output 76800k which is close to the output of your old appliance on high fire.

THATS JUST A GUESS, never just plop in whatever the last furnace was cause you dont know if THAT one was sized correctly