Title: What to do with un used flex line from cooktop ?
Post by: wantboost on January 07, 2026, 02:34:49 PM
How / where should this be capped off when going back to electric (there is a shutoff )
(What icon do I use to post a pic ?)
Title: Re: What to do with un used flex line from cooktop ?
Post by: wantboost on January 07, 2026, 08:15:44 PM
There is a small shut off valve where the flex line ends ( it's actually in the next cabinet)
1. Does a small pipe/ cap have to be added when the yellow flex line is removed ?
2.Can the flex line stay ?
3. Is a "dead leg ok on the system like this ?
Title: Re: What to do with un used flex line from cooktop ?
Post by: Admin on January 07, 2026, 10:10:42 PM
It's hard to tell but if that's two gas connecters connected together it's probably against code that they are passing through the cabinet.

QuoteClause 6.21.2
A gas connector shall
a) be protected from damage;
b) not pass through a wall, floor, ceiling, or partition;
c) be connected to rigid piping or tubing located in the same area as the appliance; and
d) comply with Clauses 4.5.2 and 4.9.1.

I would remove everything and install a nipple and cap into the shut off valve.

QuoteClause 6.12.1
During the period when an appliance is not connected to an outlet of a piping system, the outlet shall be made tight by means of
a) a plugged valve; or

b) either a cap or plug made of material compatible with the material of the piping or tubing system.
Title: Re: What to do with un used flex line from cooktop ?
Post by: wantboost on January 09, 2026, 05:48:57 AM
Where are you referring to 2 gas connectors ? Is a cabinet still considered a wall ??
Quote from: Admin on January 07, 2026, 10:10:42 PMIt's hard to tell but if that's two gas connecters connected together it's probably against code that they are passing through the cabinet.

QuoteClause 6.21.2
A gas connector shall
a) be protected from damage;
b) not pass through a wall, floor, ceiling, or partition;
c) be connected to rigid piping or tubing located in the same area as the appliance; and
d) comply with Clauses 4.5.2 and 4.9.1.

I would remove everything and install a nipple and cap into the shut off valve.

QuoteClause 6.12.1
During the period when an appliance is not connected to an outlet of a piping system, the outlet shall be made tight by means of
a) a plugged valve; or

b) either a cap or plug made of material compatible with the material of the piping or tubing system.


1. If I remove the flex hose can I cap the silver flare connection is that allowed ? The silver connection is connected to black pipe
2. If I cap after the shutoff is there a rule of how long the pipe should or should be
Title: Re: What to do with un used flex line from cooktop ?
Post by: Admin on January 09, 2026, 09:48:26 AM
I think a flex connector should only be used when there is an appliance to connect it to.

Any length nipple would be approved.
Title: Re: What to do with un used flex line from cooktop ?
Post by: wantboost on January 10, 2026, 02:31:04 PM
Does it matter pipe dope or thread tape ??
Title: Re: What to do with un used flex line from cooktop ?
Post by: Admin on January 10, 2026, 03:39:19 PM
Either as long as they have CAN/ULC-S642 certification.

QuoteClause 6.9.6
When a jointing sealant is used, it shall be certified to CAN/ULC-S642 and shall be applied to the male threads of a metal pipe. Tape shall be stretched and applied in a clockwise direction, with a 50% overlap leaving the first two starter threads bare.