www.hvactechgroup.com - forums

HVAC Forums => HVAC Help => Topic started by: SnakeDoctor on December 05, 2010, 10:51:02 AM

Title: Circulating Fan Running when it Shouldn't ?
Post by: SnakeDoctor on December 05, 2010, 10:51:02 AM
I noticed a strange thing happening on my upstairs HVAC unit a few weeks ago...

The thermostat (digital) was in the COOL mode and set to 72°.  It was a cool day and the room (per the thermostat) was about 67°.  I happened to be upstairs when the circulating fan came on.  I checked the outside compressor unit and it was not running.  I then set the mode to OFF and the fan stopped after about a minute.  I set the thermostat to HEAT mode and set it to 68° and all seemed OK until a day or two ago when the circulating fan came on when the room was about 70°.  Any ideas why this would be happening?
Title: Re: Circulating Fan Running when it Shouldn't ?
Post by: Admin on December 08, 2010, 05:17:07 PM
You may have a short in the low voltage thermostat wiring, bad thermostat or faulty fan control in the furnace.  Sometimes the fan runs if a safety trips, but unlikely if your system was off.

Is this the same unit that has been giving you heating problems?

Some thermostats have a fan on, auto and circ/prog mode.  Make sure you have it set to auto.  The Circ/Prog mode cycles the fan every so often.

What kind of furnace and thermostat do you have?
Title: Re: Circulating Fan Running when it Shouldn't ?
Post by: SnakeDoctor on December 09, 2010, 11:13:45 AM
This is not the same system that is giving me the heating problems though is is the same brand (Goodman).

It is a Robertshaw digital thermostat (not programmable).  It has 2 buttons: 1 for setpoint up and 1 for setpont down.  It also has a 3 position slider for Heat - Off - Cool and a 2 position slider for Fan Auto - On.

If I put the 3 position slider to Off and the 2 position slider to On, the fan will run.  When I put the 2 position slider back to Auto with the 3 position slider still in Off, the fan will run for about 60 seconds longer then stop.

I don't know if this had anything to do with it but I changed the batteries in the thermostat and I haven't noticed it happening since.  It seems unlikely that old batteries would cause the fan to come on though.
Title: Re: Circulating Fan Running when it Shouldn't ?
Post by: Admin on December 09, 2010, 04:26:32 PM
It still sounds like a bad control board.  Every post you've made leads me to think you have a faulty control board.  Eventually it will fail completely.