HVAC Forums => HVAC Help => Topic started by: aloosh on January 11, 2012, 10:59:26 PM

Title: fp termination clearance
Post by: aloosh on January 11, 2012, 10:59:26 PM
is it a code violation to have hydro running below a fireplace termination. wire is running in pvc conduit. its less than 2inch below where the fresh air enters the b vent.
Title: Re: fp termination clearance
Post by: Admin on January 12, 2012, 08:08:05 AM
Clause 8.18.10 of the gas code requires a minimum of 1" clearance from B-Vent to combustible material, such as PVC.  I would ask an electrician if there is any electrical code preventing your work.