www.hvactechgroup.com - forums

HVAC Forums => HVAC Help => Topic started by: Viperi on July 17, 2017, 06:17:57 PM

Title: Natural Draft water tank in a rental basement
Post by: Viperi on July 17, 2017, 06:17:57 PM
hey guys i just looked at a job and the basement is a rental. they have a natural draft water tank, and a mid eff furnace in a tiny closet by the kitchen. I read the code and i can't have it in bedrooms and washrooms but what about a kitchen as its still a living space sort of.

 Can we put back in a new natural draft tank and keep the mid furnace or both have to be changed out to a high eff furnace and a single pipe PV Hot water tank?
Title: Re: Natural Draft water tank in a rental basement
Post by: walker on July 31, 2017, 07:15:16 PM
It may not even meet code requirements in the closet its in anyways, what kind of combustion air supply is being provided to the enclosure?
Title: Re: Natural Draft water tank in a rental basement
Post by: walker on July 31, 2017, 07:45:19 PM
I don't know of any codes that prevent a water heater from being installed in a kitchen.  I only see codes preventing water heaters being installed in bedrooms & bathrooms, or enclosures accessed by bathrooms, I don't however see any codes preventing a furnace from being installed in a bathroom or bedroom.  This of course I am talking about non-direct vent appliances.

Can anyone else chime in on where you can and cant install a furnace or water that is non direct vent.
Title: Re: Natural Draft water tank in a rental basement
Post by: Admin on July 31, 2017, 08:39:57 PM
If the tiny closet had an adequate chimney, combustion air supply and the clearances were satisfied, I don't see a problem. 

Without a seperate enclosure there are certain Building Codes to consider if there are nearby return air openings.

Quote
6.2.3.20 - (6) Return-air inlets shall not be installed in an enclosed room or crawl space that provides combustion air to a fuel-fired appliance.

Quote
6.2.4.7 - (13) Return-air inlets shall not be installed in an enclosed room or crawl space that provides combustion air to a furnace.

Clause 7.27.1,

Quote
7.27.1
A water heater, unless of the direct-vent type, shall not be installed in a bathroom, bedroom, or any enclosure where sleeping accommodation is provided.
A power vent water heater may be installed in an enclosure adjacent to a bedroom or bathroom provided adequate combustion air per clause 8.2.6 is provided to the enclosure. This combustion air supply shall not be supplied from the bedroom or bathroom.
A natural draft water heater may be installed in an enclosure that is accessed by a pedestrian door which can be opened from a bathroom or bedroom, provided that the enclosure has a volume equal to or greater than the bathroom or bedroom.