HVAC Forums => Technical Information => Topic started by: Hgye on July 03, 2018, 06:28:42 PM

Title: Oil tanks
Post by: Hgye on July 03, 2018, 06:28:42 PM
Does the outlet of an oil tank need to be 1.25" until it gets into the house?  Most tanks have 1/2" copper coming out of the tank then into the house.  Another tech told me it needs to be 1.25", and I would like to confirm it.
Title: Re: Oil tanks
Post by: slo-115 on July 03, 2018, 08:21:50 PM
For outdoor tanks that are a gravity system you need to pipe into the house in 1 1/4" black iron with swing joint or 1" stainless steel connector.

Or top draw, with a 5 port oil tank. Fill, vent, suction line, gauge, and the front port is for annual water testing. Most guys go top draw wth a tiger loop at the burner. The biggest pain is the 6" thick poured cement pad with rebar. Its best to get it into the basement.
Title: Re: Oil tanks
Post by: Hgye on July 03, 2018, 08:35:51 PM
I see Wolseley still sell double bottom Granby Ecogard tanks with 1/2" outlets.  So these tanks cannot be installed outdoors anymore?
Title: Re: Oil tanks
Post by: slo-115 on July 04, 2018, 09:04:11 PM
Correct only inside with a tank containment tray underneath.

149001 inside tank 1/2" bottom.Fill,vent,gauge

149003 outside gravity fed 2" bottom. Fill,vent, gauge.

149303 outside top draw. 2" bottom (capped) Fill,vent, gauge,water test port.