HVAC Forums => Technical Information => Topic started by: PeterT on October 26, 2007, 10:00:57 PM

Title: Direct vent Fireplace
Post by: PeterT on October 26, 2007, 10:00:57 PM
On a direct vent gas fireplace under 100,000BTUS is there the same clearance to window openings and building openings as there are for gas furnace vent terminations in Ontario by the TSSA. I am trying to find the clause in the new code book.
Title: Re: Direct vent Fireplace
Post by: Admin on October 27, 2007, 02:51:25 PM
Clause 8.14.8 pertains to all vent terminations.  Unless your installing a pool heater use the table below.  The pool heater needs 10' from a building opening as per Clause 8.14.10.

Quote(8.14.8) A vent shall not terminate
(a) directly above a paved sidewalk or paved driveway that is located between two single-family dwellings and serves both dwellings; This does not apply to non-condensing appliances;
(b) less than 7 ft above a paved sidewalk or a paved driveway that is located on public property;

10,000 - 100,000 BTU's

(c) (d) (e) (f) (g)                                                                            
Mechanical air supply  = 6'                                                 
Regulator vent outlet = 3'                                        
Grade level = 1'                                        
Window and door = 1'                                                                                           
Non mechanical air supply = 1'
Combustion air inlet = 1'   


You only need 1' from a window.
Title: Re: Direct vent Fireplace
Post by: PeterT on October 28, 2007, 03:20:33 PM
So if someone has installed a direct vent fireplace with less than 1 foot from a window that opens what are the consequences. Why I ask is someone has come to me as they see my truck in the driveway all the time and a neighbour of their's has installed a gas fireplace and the neighbour can smell the fireplace coming in their window. I don't want to get into a neighbour hood fight over it but was asked what the code said. And what they could do about it.
Peter
Title: Re: Direct vent Fireplace
Post by: Admin on October 28, 2007, 04:48:05 PM
This person's neighbour has a fireplace termination less then 1' from their own window???  These houses must be built close together!

Well there are only 2 ways to comply to the code.

1. Follow Director's Advisory FS-106-07 (http://hvactechgroup.com/files/advisory/fs10607.pdf) and make the window unopenable.
2. Relocate the termination

Obviously the neighbour should not have to seal the window.  I would force the owner of the fireplace to relocate the termination.
Title: Re: Direct vent Fireplace
Post by: PeterT on October 28, 2007, 07:03:56 PM
No the window that the neighbour is asking about is the one in the house that has the fireplace that is less than 1 foot away. He says he can still smell it when the wind blows the right way. I guess he is looking for away to get the neighbour to move it.