QuoteClause 6.9.6
When a jointing sealant is used, it shall be certified to CAN/ULC-S642 and shall be applied to the male threads of a metal pipe. Tape shall be stretched and applied in a clockwise direction, with a 50% overlap leaving the first two starter threads bare.
Quote from: Admin on January 07, 2026, 10:10:42 PMIt's hard to tell but if that's two gas connecters connected together it's probably against code that they are passing through the cabinet.QuoteClause 6.21.2
A gas connector shall
a) be protected from damage;
b) not pass through a wall, floor, ceiling, or partition;
c) be connected to rigid piping or tubing located in the same area as the appliance; and
d) comply with Clauses 4.5.2 and 4.9.1.
I would remove everything and install a nipple and cap into the shut off valve.QuoteClause 6.12.1
During the period when an appliance is not connected to an outlet of a piping system, the outlet shall be made tight by means of
a) a plugged valve; or
b) either a cap or plug made of material compatible with the material of the piping or tubing system.
QuoteClause 6.21.2
A gas connector shall
a) be protected from damage;
b) not pass through a wall, floor, ceiling, or partition;
c) be connected to rigid piping or tubing located in the same area as the appliance; and
d) comply with Clauses 4.5.2 and 4.9.1.
QuoteClause 6.12.1
During the period when an appliance is not connected to an outlet of a piping system, the outlet shall be made tight by means of
a) a plugged valve; or
b) either a cap or plug made of material compatible with the material of the piping or tubing system.