Quote9.33.6.11 - Warm-Air Supply Outlets
(3) Where the heating system is also designed to provide ventilation air, ceiling outlets or outlets located high on interior walls are permitted to be installed, provided the outlets are designed for this purpose and are installed with diffusers.
Quote9.33.6.12 - Return-Air System
(2) Except for floor levels which are less than 900 mm above or below an adjacent floor level which is provided with a return-air inlet, at least one return-air inlet shall be provided in each floor level in a dwelling unit.