Soft Start Install Question

Started by rfc2005, September 09, 2024, 11:39:58 PM

Previous topic - Next topic

rfc2005

I want to install an ICM870-16A Soft Start on a Carrier GH5SAN 430-A.

The instructions state "not to be used on units that have control boards that sense compressor current and perform a lock out for fault conditions".

How do I check this unit to make sure it does not have that lock out feature on the board?

Thank you, Bob

Porcupinepuffer

Quote from: rfc2005 on September 09, 2024, 11:39:58 PM"not to be used on units that have control boards that sense compressor current and perform a lock out for fault conditions".


That unit doesn't do that. You should be fine.