Honeywell T10+ with Redlink 3.0

Started by Benny, May 13, 2025, 07:06:44 PM

Previous topic - Next topic

Benny

Honeywell T10+ with Redlink 3.0 (THX321WF3003W) plus 2 wireless indoor sensors (C7189R3002) and 1 wireless outdoor sensor (C7089R3013)

Goal is to have this t-stat control humidifier with heat and independent of call for heat when heat is not needed.

Humidifier is Aprilaire 550 bypass. Furnace is Trane TUD100C948K4.
Furnace board is CRYGW / Twin and current stat is RYGN with R jumped to RC (assume one transformer). Furnace does not have optional hum and EAC board.

Planned install
Redlink 3.0 only for communication – no app – also no WIFI will be available Will use 2 wireless room sensors and 1 outside temp sensor.

AC Furnace C and Y to outside unit

Tstat CGRW to same on furnace (R slider on stat up-one wire)

Tstat Hum U and U wires – this is where I need a little help.
As current – one u to W(heat) the other to hum solenoid wire 1 and then solenoid wire 2 back to C
OR - one u to G(fan) the other to hum solenoid wire 1 and then solenoid wire 2 back to C
OR – one u to solenoid wire 1 and the other u to solenoid 2
OR – add transformer and one u to hum solenoid wire 1, solenoid wire 2 to new transformer C and other U wire to new transformer R
OR – something else?

My question is will this stat handle the call for hum without heat or will I need an extra transformer or do I need to change wiring set up?