GAS RANGE CODE QUESTION

Started by scarey8, April 17, 2013, 07:50:15 PM

Previous topic - Next topic

scarey8

curious if anyone can come up with a clause or requirement that demands that a gas range in a residential home is required to be vented directly to outdoors...  nothing in the section under gas ranges other than clearances and such.   there is a section in venting 8.9.1 of the 2005 code ( new book is in the van)    it states that every appliance shall be connected to either an effective chimney or a vent, except
radiant heaters,
appliances that are approved for use without a vent
etc. 

as a rule always read the manufacturer instructions regarding install, anyone ran into this issue?

I know that the DA domestic appliance tech can work on unvented appliances up to 75 000 btuh i believe, being that ranges are domestic appliances this would be a shot in the dark. 

advise please

scarey

Admin

It depends on what the manufacturer of the range and range hood state in their manuals.  There are no gas codes that I know of that enforce the use of range hoods.  Even if a range hood was installed, only the client can decide if they want to turn it on.

B149.1-10 Clause 7.32.8,

QuoteClause 7.32.8 - An exhaust hood, an exhaust appliance, or a combination thereof installed above a range shall be installed in accordance with certified installation instructions for such an exhaust hood or appliance.

Ontario Regulation 215/01 Section 31,

QuoteDA Certificate - 31.  (1)  A person who is the holder of a DA certificate may install, alter, purge, activate, repair, service or remove any unvented residential natural gas or propane gas appliance and its equipment or a vented refrigerator that has an input of 100,000 Btuh or less, other than a construction heater.  O. Reg. 215/01, s. 31 (1).

(2)  When performing a function described in subsection (1), the person may also do the following:

1.Install, test, inspect, activate, alter, purge, service, repair or remove any piping or tubing or component in a piping or tubing system to an unvented residential appliance or vented refrigerator downstream of the natural gas meter or propane vapour service valve.

2.Maintain, service or replace a mechanical or electrical component or moisture duct or accessory that forms part of an unvented residential appliance or vented refrigerator and that is essential to the appliance's operation.

3.Perform the tasks that are necessary to replace controls, components and accessories that form part of an unvented residential appliance or vented refrigerator and that is essential to the appliance's operation.

4.Service and replace electrical switches, fuses, components and control wiring that are directly related to the operation of an unvented residential appliance or vented refrigerator.  O. Reg. 215/01, s. 31 (2).


The Building Code is what requires us to install a range hood and exhaust duct.

Quote9.32.3.5. Supplemental Exhaust
(2) An exhaust air intake shall be installed in each kitchen, bathroom and water closet room.
(4) Exhaust ducts serving the required kitchen, bathroom, water closet room and other supplemental exhaust air intakes shall be sized according to Part 6 except that they may be sized according to Table 9.32.3.5. where,
(a) the total duct length does not exceed 9 m, and
(b) the number of elbows does not exceed 4, but, in any case, they shall not be smaller than recommended by the manufacturer of the fans.