What would cause high carbon monoxide levels in a mid-efficiency furnace (800PPM) ?? I was working on one today and took a reading and it was really high and I didn't know what the cause of this could be.

Any insight would be great, thanks in advance.


Admin

I would check the manifold gas pressure and lower it if required.  An overfired furnace can create up to 4500 PPM.  A small adjustment can lower this down to 20 PPM.

What kind of furnace were you working on?

walker

It was a keeprite, I did check the manifold and it was running at 3.5"w.c.

Can any other issues cause high CO?

Admin

Make sure the burners are in good shape and clean.  Does the flame look good?

Those furnaces have had alot of heat exchanger failure so I'd look for cracks.

walker

I did a camera and visual inspection of the heat exchanger, and everything looked good, that's why I'm puzzled as to the high reading, flame was good as well.

slo-115

There were some tough years with those icp products. If possible cut a inspection door in the hot air plenum and check for "poped" heat exchanger rings. Sometimes if you pull the blower fan you can find those rivet rings laying down there

harshal

FOUND TODAY POPPED RING IN THE ICP.M-CUG5075BFA2.WAS ALMOST 20 YRS OLD MID.SOMETIMES U CAN FIND THE POPPED RING THROUGH THE LIMIT HOLE/OTHERWISE I OPEN UP THE PLENUM AND CHK FOR ALL THE PASSES UPTO BOTTOM .BCOA THEY ARE MORE LIKELY TO POOPED UP BCOZ OF HIGH HEAT OR CLOSE TO BURNER AREA I MID FURNACE.THE HIGH CO COULD BE RESULT OF PARTIALLY BLOCKAGE IN COLLECTOR BOX/I WOULD OPEN UP N VACCUM IT OUT N REPLACE THE GASKET IF REQ.