Last to touch rule

Started by Mmtc79, January 23, 2019, 08:26:32 PM

Previous topic - Next topic

Mmtc79

Hey guys hope all is well !
I'm getting asked about last to touch is now responsible !  Or last fitter on site is liable ?

Example gas tech goes to install new appliance upon completion he gives a check of all other gas pipes , venting and other appliances to confirm all is up to code
He finds some issues ? Do you walk away cause you did not touch that portion of system or appliance or do you tag with appropriate a or b tag ? I know the correct answer but curious to see the reply's to the question will be

Cheers

Admin

I would always protect myself and the client and issue an immediate or non immediate warning tag, as per O.Reg 212/01.

Porcupinepuffer

It's what's within your line of sight in relation to where you're working. You're not required to do a complete inspection of all appliances within the dwelling. If you were at a residence just to change a water heater, you wouldn't be responsible as the last person on site if a fireplace in the master bedroom on the second floor was a major hazard that you could only identify by actually being in that room.

Attavior

Seasonal boiler check requires you to check. 


7.1.12.1
During each heating season effective October 15th to April 30th when a certified G1, G2, G3 or GUT gas technician enters a residential building intended for one or two single families to carry out service, maintenance and/or emergency response work within the scope of his/her certificate, the gas technician shall:

Hvacpimp

Quote from: Attavior on January 25, 2019, 07:06:21 AM
Seasonal boiler check requires you to check. 


7.1.12.1
During each heating season effective October 15th to April 30th when a certified G1, G2, G3 or GUT gas technician enters a residential building intended for one or two single families to carry out service, maintenance and/or emergency response work within the scope of his/her certificate, the gas technician shall:
Is this even what we are talking about??? Are you confused?? What does the annual boiler inspection have anything to do with the question?
Porcupinepuffer is right but you better believe that if something did happen you would be questioned for it but probably wouldn't get orders for it.  Another rule of thumb is if it has been worked on in the last 6 months. Believe me, when I have to write a report, one of the first questions tssa asks is the 6 month rule.


Porcupinepuffer

Actually, that natural draft boiler requirement does directly relate. I think it would around mid-2000's they sent out the memo for any gas tech who's last on site at a residence with a natural draft boiler to make sure it's tagged with the annual inspection. The spillage of neglected boilers was a big issue. Putting it on our shoulders was the solution.

Hvacpimp

Sorry I didn't read it right because I was half in the bag when I responded. It all comes down to the 6 month rule. The natural draft boiler clause that was pointed out was an example. We could go on for hours like that. Broken vent, leaking union, etc. As you said before line of sight. Me personally, when I was an installer, if I was doing a fireplace, I would take a quick look at the furnace. Takes 2 seconds and could save grief. It's all luck and common sense.