« on: March 27, 2019, 08:23:59 AM »
Aside from what the code book states, are there any TSSA bulletins or documents with regard to repairs of commercial/i dustrial heat exchangers? Code states they may be repaired in accordance with the authority having jurisdiction. 
Specifically can a heat exchanger on a commercial make-up air unit be welded even if the manufacturer does not have a procedure for it and does not endorse it?
My  opinion would be no but am wondering if the TSSA has a written policy.
Thanks.

Offline viking

  • Pro Tech™
  • *****
  • Posts: 52
Re: Commercial Heat Exchanger Repair
« Reply #1 on: March 27, 2019, 09:10:31 AM »
I believe I found the answer in FS-099-07

Offline Admin

  • Administrator
  • *****
  • Posts: 2508
    • HVAC TECH GROUP
Re: Commercial Heat Exchanger Repair
« Reply #2 on: March 27, 2019, 09:18:48 AM »
Interesting, that Advisory was not posted here.  I noticed it says,

Quote
To apply for the required approval of the repair procedure, the following shall be submitted to the Director of Fuels Safety Program, by completing a variance application form:
1. Complete description of the repair process. Where the process includes welding, include the welding procedure in the CWB or ASME format;
2. Make and Model of the appliance; and,
3. Letter from the appliance manufacturer accepting the repair procedure. If the manufacturer is no longer in business, the repair procedure shall be reviewed and accepted by a Professional Engineer.

Download TSSA Advisory FS-099-07-R1 - Here

Offline viking

  • Pro Tech™
  • *****
  • Posts: 52
Re: Commercial Heat Exchanger Repair
« Reply #3 on: March 27, 2019, 06:22:19 PM »
Thanks Admin.
I also got some info from the manufacturer.
They do have a procedure for welding there heat exchangers