Author Topic: ask for approach temp and space temp  (Read 116 times)

Offline teeckg

  • 313D Supporter
  • ****
  • Posts: 17
ask for approach temp and space temp
« on: June 10, 2019, 12:55:39 PM »
I have one point don't sure.
the question gives Sapce temp=15, Approach temp 5, what is the air leaving temp?
   15-5=10 ?     or leaving temp=space temp=15 ?

Offline Admin

  • Administrator
  • *****
  • Posts: 2356
    • HVAC TECH GROUP
Re: ask for approach temp and space temp
« Reply #1 on: June 10, 2019, 06:46:43 PM »
I was taught the approach temperature is the difference between your liquid line temperature and the outdoor ambient temperature.  For example if the liquid line temperature was 90°F and the outdoor temperature was 85°F the approach temperature would be 5°F.

I attached pictures below from a Lennox installation manual that explain how to use the approach method.