Started by always something, October 01, 2023, 08:31:07 PM

Previous topic - Next topic

always something

My T'STAT is calling for heat but the blower is not activating. The boiler is turning on and sending hot water to the air handler. The blower works as it runs when the T'stat is turned to on and the AC setting turns the same blower on.

Thoughts?

Cheers!

Admin

If you turn the thermostat fan from AUTO to ON does the fan run?

What model of air handler do you have?  It could be a faulty relay on the control board.

always something

Yes, blower works fine when set to On. Also, the AC setting activates the same blower in the Auto setting.

Unit is a Carrier. House built in 1988.

Thanks

always something

Here is a picture of the nameplate.

always something

Here are some additional photos of the controls. Not much to this one.

Admin

Is this a heat pump system?  Or do you only use the hydronic heating?

There's probably an issue with that Honeywell control.  Turn the heat on and try to turn that dial down and see if the fan starts.

always something

In a separate room is a slant fin boiler. This pumps water over to the handlers for air flow upstairs. It also pumps water throughout the basement as a hydronic like system. Adjusting that knob does nothing while calling for heat.

What is the device supposed to do or protect? It is measuring the temperature of the hot water pipe coming into the air handler.

Suggestions on how to get a replacement part number for the Honeywell controller?

Appreciate the help.

always something

Found the Honeywell part number. T675A/ Looks like a simple R&R project.