Can someone can tell me where to find gas piping charts for propane in the B149.1-05 or B149.1-10 Natural gas and propane code.

Offline Hgye

  • Pro Techâ„¢
  • *****
  • Posts: 80
Re: B149.2 Propane Code
« Reply #1 on: October 15, 2012, 08:10:06 PM »
Annex B of 149.1

Offline Admin

  • Administrator
  • *****
  • Posts: 2364
    • HVAC TECH GROUP
Re: B149.2 Propane Code
« Reply #2 on: October 15, 2012, 09:40:08 PM »
Lol thanks!

I must have flipped through my code book 20 times looking for that.  I don't do much work on propane.

Offline Rustymike

  • ***
  • Posts: 11
Re: Propane gas sizing
« Reply #3 on: November 16, 2012, 10:32:22 PM »
AS a superior propane contractor with a fitter 1 cert in both gas and propane, even before they got combined into the 1 cert, you can usually get away with using the nat gas pipe sizing chart for most gas loads until you get into higher loadings (over 500MMbtu) or your running a longer gas line across a roof.