air at 90 db and 70 dp is cooled to 65db and 58 dp.how much heat is removed in btu/lb in the process?

40.0 Btu/lb
1 (16.7%)
28.0Btu/lb
1 (16.7%)
14.0Btu/lb
0 (0%)
12.75Btu/lb
4 (66.7%)

Total Members Voted: 6

Author Topic: AC question  (Read 1793 times)

Offline piru

  • 313D Supporter
  • ****
  • Posts: 6
AC question
« on: February 11, 2016, 07:36:16 PM »
let me know how to find the answers

Offline Admin

  • Administrator
  • *****
  • Posts: 2363
    • HVAC TECH GROUP
Re: question
« Reply #1 on: February 17, 2016, 08:32:00 PM »
I'm not 100% sure I'm right.

We use a Psychrometric Chart to solve this problem.

A Dry Bulb of 90F and a Dew Point of 70F would give us a Wet Bulb of 75.6F, a Relative Humidity of 52% and Enthalpy of 39.55 BTU/lb.

A Dry Bulb of 65F and a Dew Point of 58F would give us a Wet Bulb of 60.6F, a Relative Humidity of 78.1% and Enthalpy of 26.8 BTU/lb.

39.55 BTU/lb - 26.8 BTU/lb = 12.75 BTU/lb.

I attached a copy of the Psychrometric Chart I used.  Hopefully it makes sense, it's been 20 years since I used one  ;D

Offline Porcupinepuffer

  • Pro Techâ„¢
  • *****
  • Posts: 457
Re: AC question
« Reply #2 on: February 19, 2016, 10:07:15 AM »
The psychrometric chart I used is different, but I got 12.6 btu/lb. Mine has the wb and dp temperatures on the left side and uses the horizontal lines for dp numbers and wb lines are angled downward.

Offline Admin

  • Administrator
  • *****
  • Posts: 2363
    • HVAC TECH GROUP
Re: AC question
« Reply #3 on: February 19, 2016, 11:06:37 AM »
Yes I believe all his available answers are wrong.  The enthalpy for a DB of 90F and DP of 70F is actually 38.95 BTU/lb.

38.95 - 26.87 = 12.08 BTU/lb.