Author Topic: Beckett Oil Burner HELP!  (Read 4054 times)

Offline smithkors

  • ***
  • Posts: 1
Beckett Oil Burner HELP!
« on: January 03, 2010, 07:57:54 PM »
We have a Beckett Oil Burner that keeps tripping. My husband has changed the thermostat, the oil filter, and the nozzle. Any ideas? Please help! Thanks!
Renee

Offline dmfv

  • G2 Supporter
  • ****
  • Posts: 17
Re: Beckett Oil Burner HELP!
« Reply #1 on: January 04, 2010, 05:44:42 PM »
more info would help? how many times has the reset button been pushed? if more than once I wouldnt try fixing it, call a professional or you will burn your house down...

Offline Admin

  • Administrator
  • *****
  • Posts: 2405
    • HVAC TECH GROUP
Re: Beckett Oil Burner HELP!
« Reply #2 on: January 05, 2010, 02:28:10 PM »
I don't have alot of oil experience, but I would check the cad cell.  It may be dirty and can't see the flame, causing the unit to trip.
The primary control or a weak ignition transformer may also cause the unit to trip.

Offline ALPHADOG3

  • 313D Supporter
  • ****
  • Posts: 2
Re: Beckett Oil Burner HELP!
« Reply #3 on: January 10, 2010, 01:10:11 PM »
sounds as maybe your ignition transformer is weak ( call a pro, you don't want to test youself) as their is EMTREMELY high secondary voltage involved.  doing the things you did already (filter and nozzle) are both great starts.  You could also try tapping the top of the primary control (gray box) beside the transformer.  Sometime the points on the contacts inside become warn and weak and can drop out without notice.