vent wont comes On when starting furnace after replacing ignitor/ pilot

vent not blocked
0 (0%)
safety on fail
1 (100%)

Total Members Voted: 1

tozrin

vent wont comes On when starting furnace after replacing ignitor/ pilot on a keeprite upflow furnace

Admin

Are you refering to the main blower fan?

Do you have central AC?  Did you try switching the thermostat to fan ON?  Does the fan run?

There may be a faulty fan timer in that furnace or control board.

What's the model #?

tozrin

i m talking about exahust fan, , should'nt be  timer, as no place for it,. no AC in the unit..Thanks

Admin

It's probably the control board, unless you pulled the ventor motor wiring out of the molex connector when you replaced the ignitor.

Verify if you're getting 120V from the control board terminal that feeds the black wire to the ventor motor.

tozrin

ya the 120V going to the fannot stable/intermittent!..may the board as you mentioned,Thanks ADMIN..........

Admin

No problem!

Just make sure you have a constant 24V at the W terminal on the control board to rule out any possible low voltage wiring or thermostat problem.