I should probably know this, but I haven't done this in ages. So here I am. Anyone know how to know if your meter is big enough for the asking load? Does it say anything on the meter itself? Parents want add a few things that will add more btu's.

Thanks!

Offline Attavior

  • ***
  • Posts: 53
Re: Meter Sizing
« Reply #1 on: October 30, 2017, 08:16:40 PM »
What class is the meter (200 or 400)?  If it's a 200 class it's good fur 300000 btuh, 400 is good for 600000 btuhs @ 7" w.c.   

Offline nash668

  • G2 Supporter
  • ****
  • Posts: 56
Re: Meter Sizing
« Reply #2 on: December 10, 2017, 01:08:55 PM »
I don't even know how to tell...

5m³ at a drop of 0.125kpa...

Offline Admin

  • Administrator
  • *****
  • Posts: 2300
    • HVAC TECH GROUP
Re: Meter Sizing
« Reply #3 on: December 10, 2017, 02:49:08 PM »
I think the 250 has a 1” outlet and the 400 has a 1-1/4” outlet.  There should be a metal tag on the gas meter that lists the model.