7.27.1 ?
« on: October 04, 2017, 06:15:23 PM »
So I looked @ a gas re / re furnace only
Upon entering basement totally finished basement cx says furnace and hwt are in the bedroom upon entering open a door in room find a mid furnace and a cv tank that had just been changed out by one of the large rental company's room with equipment is small no combustion air at all tank was replaced less the. A yr ago why are they not fixing problems and leaving stuff not to code then the honest guy comes in and looks like a dickhead to the customer for doing his job then the question is why did they do this ? Is anyone else finding these gems or is there a easy way to remedy this otherwise then taking bed out of the room lol

Offline tenletters

  • 313D Supporter
  • ****
  • Posts: 61
Re: 7.26.1 ?
« Reply #1 on: October 04, 2017, 07:38:15 PM »
Hopefully you didn't write 7.26.1 on your infraction ;)

7.27.1
A water heater, unless of the direct-vent type, shall not be installed in a bathroom, bedroom, or any
enclosure where sleeping accommodation is provided.

Write up the infraction and move on. His bill will increase $10 with his rental company. They'll cap off the venting and throw in a new tank if the customer wants.

Offline walker

  • Pro Tech™
  • *****
  • Posts: 490
Re: 7.26.1 ?
« Reply #2 on: October 04, 2017, 08:19:54 PM »
I run in to this all the time.  I usually B-tag, tell the customer if I don't see a bed, its not a bedroom.  They make the bed disappear, the b-tag gets cleared, then magically later on long after I'm gone the bed will reappear, I've covered my ass by b-tagging it and the customer understands they can't have a bed in that room, if something goes south that's now on them.

Offline Mmtc79

  • Pro Tech™
  • *****
  • Posts: 31
Re: 7.26.1 ?
« Reply #3 on: October 04, 2017, 09:15:10 PM »
No I wrote 7.27.1 lol typo lol

Offline Admin

  • Administrator
  • *****
  • Posts: 2106
    • HVAC TECH GROUP
Re: 7.27.1 ?
« Reply #4 on: October 05, 2017, 05:30:41 AM »
Keep in mind Clause 7.27.1 was amended by FS-225-17 in the B149.1-15 Code.

Quote
Clause 7.27.1 is revoked and the following substituted for it:

Clause 7.27.1 - A water heater, unless of the direct-vent type, shall not be installed in a bathroom, bedroom, or any enclosure where sleeping accommodation is provided.

A power vent water heater may be installed in an enclosure adjacent to a bedroom or bathroom provided adequate combustion air per clause 8.2.6 is provided to the enclosure. This combustion air supply shall not be supplied from the bedroom or bathroom.

A natural draft water heater may be installed in an enclosure that is accessed by a pedestrian door which can be opened from a bathroom or bedroom, provided that the enclosure has a volume equal to or greater than the bathroom or bedroom.

I only install direct vent appliances.  Does this mean it's okay that a mid efficiency furnace is installed in a bedroom?  The only concern is with the water heater?

Offline Frosty

  • Pro Tech™
  • *****
  • Posts: 6
Re: 7.27.1 ?
« Reply #5 on: October 05, 2017, 02:04:50 PM »
Is that some sort of sharbite CF adaptor fitting coming off the hot and cold lines?

Offline Porcupinepuffer

  • Pro Tech™
  • *****
  • Posts: 410
Re: 7.27.1 ?
« Reply #6 on: October 05, 2017, 07:15:20 PM »
Is that some sort of sharbite CF adaptor fitting coming off the hot and cold lines?

Sure looks like it.

Offline Mmtc79

  • Pro Tech™
  • *****
  • Posts: 31
Re: 7.27.1 ?
« Reply #7 on: October 05, 2017, 09:12:18 PM »
Yeah it's a shark bite fitting and yes direct vent all the way and yes the furnace is a problem but that's getting replaced now water heater is getting replaced with a pvdv so all good to go

Offline walker

  • Pro Tech™
  • *****
  • Posts: 490
Re: 7.27.1 ?
« Reply #8 on: October 06, 2017, 12:37:47 PM »
whats the problem with the furnace?

Offline Mmtc79

  • Pro Tech™
  • *****
  • Posts: 31
Re: 7.27.1 ?
« Reply #9 on: October 06, 2017, 03:16:10 PM »
No problem just upgrading